Dear,
I would like to know about the design of dowels that connect the old and new concrete in cases of jacketed members. Therefore, I would like to know how the demand and the capacity of dowels are computed. What are the references? Is the concrete contribution ignored?
Enes
Design of dowels
- seismosoft
- Posts: 1316
- Joined: 06 Jul 2007, 04:55
Re: Design of dowels
The values for the calculations for the dowels are calculated according to expression from the Greek Interventions Code (KANEPE) which is the only standard worldwide (that we know of), which provides an explicit methodology for such calculations.
The concrete contribution is ignored in the transfer of forces between new and old concrete.
Seismosoft Support
The concrete contribution is ignored in the transfer of forces between new and old concrete.
Seismosoft Support
Re: Design of dowels
Thank you for the reply. To which section of KANEPE are you referring, could you please share a link?
Re: Design of dowels
Dear E.Veliu,
It is available in section 8.2.1.5 of Greek Interventions Code (KANEPE).
It is available in section 8.2.1.5 of Greek Interventions Code (KANEPE).
Zoi Gronti
Seismosoft Srl.
Seismosoft Srl.
Re: Design of dowels
Dear Zoi,
Any reference on how you compute the demand? I am asking as I would like to make some hand calculations.
Enes
Any reference on how you compute the demand? I am asking as I would like to make some hand calculations.
Enes
Re: Design of dowels
Dear E.Veliu,
Please check equation S8.6 of section 8.2.1.5 of Greek Interventions Code (KANEPE).
Please check equation S8.6 of section 8.2.1.5 of Greek Interventions Code (KANEPE).
Zoi Gronti
Seismosoft Srl.
Seismosoft Srl.
