Range check error

04-Unexpected behaviour/errors
Post Reply
sybylla82
Posts: 2
Joined: 06 Mar 2012, 12:12

Range check error

Post by sybylla82 »

on the same model, we first performed a dynamic analysis
with time-history
and elements infrmFb
and analysis
has been successful ...
Then on the same model, we performed
the same analysis
using elements infrmDB
and the program gives the message "Range Check Error".
We tried to overcome the problems by following one of the above procedures, but the error always appears.
I tried to run the analysis of the eigenvalues #8203;#8203;with the same model and do not converge
Mary
Stelios_Antoniou
Posts: 89
Joined: 17 Jul 2011, 20:08

Re: Range check error

Post by Stelios_Antoniou »

Since the eigenvalue analysis does not convernge, it seems that the models prabably has some kind of error (otherwise it should give some eigen-solutions)

Does the model with the force-based elements converge in eigenvalue analysis?
sybylla82
Posts: 2
Joined: 06 Mar 2012, 12:12

Re: Range check error

Post by sybylla82 »

you .... by the eigenvalue analysis I can get the results
Mary
Stelios_Antoniou
Posts: 89
Joined: 17 Jul 2011, 20:08

Re: Range check error

Post by Stelios_Antoniou »

It seems very strange that the same model runs fine with infrmFB and not with infrmDB. Is it exactly the same model, i.e. you simply replace the infrmFB element classes with infrmDB ones? Or have you changed other things as well?
One more thing: What are the interstorey drifts that you get? Is your structure in the inelastic range, or is it still in the elastic range?
User avatar
seismosoft
Posts: 1316
Joined: 06 Jul 2007, 04:55

Re: Range check error

Post by seismosoft »

Dear Mary,

We have looked into your model and, as anticipated, did find some modelling inadequacies, such as:
- 'infrmDB' elements are not discretised, as suggested in the Help System and this Forum
- the walls' reinforcement distribution seems wrong, with a peculiar concentration in the middle of the section (see e.g. section 'ssetto1')
- the walls' confined edges cover the entire width of the wall (i.e. there is no wall web), which, again, does seem unusual
- structural walls are modelled by means of an equivalent beam, rather than an equivalent column, as suggested in this Forum and the literature
- the use of L-shape wall sections to model corner beams is, again, not common. You should use instead a T-section (with an "eccentricity" of zero)

Of course, despite the aforementioned modelling problems, the program should certainly not be giving 'range check errors', and we can confirm that such issue has now been corrected, for the forthcoming release.

Seismosoft Support
Post Reply

Return to “04-Unexpected behaviour/errors”